bphgravity
Senior Member
- Location
- Florida
If a gfci device were installed in a location that gfci protection is not required, should that gfci be required to be connected correctly and operate correctly?
My vote is it would be required to be installed the correct way.110.3 (B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
Aha. A scofflaw!Originally posted by peter d: The answer from a legal perspective is "yes." Now, the answer I would give is "no."
Ditto.Originally posted by jwelectric:
My vote is it would be required to be installed the correct way.110.3 (B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
is there any requirement it be wired at all? is there any code that says you can't have a dead receptacle?Originally posted by LarryFine:
You could draw a parallel: if you install an extra receptacle between two that are placed to comply with spacing requirements, shouldn't that extra receptacle be wired correctly?
There is no such requirement. But that is not the issue. The issue is that if it is wired, must it be wired correctly?Originally posted by petersonra:Is there any requirement it be wired at all? Is there any code that says you can't have a dead receptacle?
If you refer to the definition of receptacle and outlet in Article 100, one could say a "dead receptacle" does not meet the NEC's definition of "receptacle".is there any requirement it be wired at all? is there any code that says you can't have a dead receptacle?