The ampacity tables are all based on the conductors being in either a 30°C or a 40°C ambient. Where the ambient temperatures exceed those values, the ampacity of the conductor is required to be reduced. Table 310.15(B)(2) is for messenger supported conductors and the ampacity of the conductors in that table are based on an ambient of 40°C. Using that table, if you have a 8 AWG copper conductor in the first, 75°C, column, its ampacity is 57 amps. If you are installing that conductor in a 50°C ambient, you have to "correct" the ampacity. Using Table 310.15(B)(2)(b) we find that the correction factor for a 75°C conductor in a 50°C ambient is 0.85. The corrected ampacity is 57 x 0.85 or 48.45 amps. That is the maximum current carrying capacity of the conductor under that condition and the load and the overcurrent protective device should not exceed the corrected ampacity. Note the ampacity tables that are most commonly used have the conductor ampacities based on 30°C and the correction factors for those conductors are found in Table 310.15(B)(2)(a).