proper wiring technique

Status
Not open for further replies.
UL White Book
RECEPTACLES (RTDV)

Terminals of the wire-binding screw, setscrew, or screw-actuated backwired
clamping types are suitable for use with both solid and stranded
building wires.
 
Does the 2014 NEC allow for stranded wire to be wrapped on a screw terminal. Please give a code reference
Welcome to the Forum, Walter.

What you are dealing with, is that the language of the NEC is permissive. Or, to say it another way, if the NEC doesn't specifically say "It can't be done," - or - "It must be done this way," then it is permitted.

The applicable Code reference is 110.14.Fortunately, this passage is not 100% "silent" about solid vs. stranded. The second paragraph refers you to Chapter 9 Table 10, where you will find common 19 strand conductors included.
 