electrick1117
New member
- Location
- Fl
I'm installing a 75kva 480/208 delta-wye xfmr (it's what we had on hand) to feed a 60HP 3Ph. 208 air compressor. The compressor will be located outside the main building. There is a 480 volt 3PH 200A disconnect in the remote building fused for 110A that is fed from a 150A breaker inside which I will use for the primary. I will install a new 200A switch for the compressor main disconnect. There is an egc run with the primary conductors. Here's where the confusion comes in. Although there is a wye secondary, I do not need a neutral ran to the compressor. Do I still ground xo using the egc from the primary feed then bond to the xfmr case? Or, just leave xo open and bond the egc to the xfmr ground. To top it off, the remote building is cast concrete with only the roof being possibly connected to any of the main building metal. Should I also drive a ground rod as a supplemental ground.