A Contractor has an LB installed on a 4" conduit with (4)-600Kcmil (1)-#2(G).
The opening for the LB is only 14".
Per the 2017 NEC Article 314.28 (3) - I think I understand that unless the LB is marked with the maximum number of conductors and the maximum size then this LB is not of the proper size?
In my history i have never seen an LB that was marked for more then a maximum of 3 conductors?
The opening for the LB is only 14".
Per the 2017 NEC Article 314.28 (3) - I think I understand that unless the LB is marked with the maximum number of conductors and the maximum size then this LB is not of the proper size?
In my history i have never seen an LB that was marked for more then a maximum of 3 conductors?