This relates to increasing the EGC in proportion to the CM increase in conductor size under 250-122(b). (In CA, we're still using the '99 NEC, where this was only required for increases due to voltage drop, but I understand the 2002 code requires an EGC increase if the circuit conductors are increased for derating as well.)
If you have to increase the conductor size for derating or voltage drop and have to go from 1 conductor per leg to parallel conductors, you can have an increase in ampacity with a decrease in total CM of the conductors.
For example: 208Y/120 3 phase 4 wire feeder for 500A continuous nonlinear load. Standard OCPD is 700A. Suppose you're using 90C Cu wire with 75C terminals. Then the minimum conductor size for the load (at 75?C terminal rating) is 1500MCM good for 625A. But with a current-carrying neutral, you have to derate the 90C ampacity of 705A for 4 conductors at 80% = 564A. So you increase the conductors to 2 parallel 500MCM in 2 pipes. The total derated ampacity is 688A and using the next larger size OCPD, it works.
So, you've increased the total ampacity but decreased the total CM's from 1,500,000 to 1,000,000.
The EGC required by Table 250-122 for a 700A OCPD is 1/0 Cu.
Do you increase the EGC from this and by what calculation?
If you have to increase the conductor size for derating or voltage drop and have to go from 1 conductor per leg to parallel conductors, you can have an increase in ampacity with a decrease in total CM of the conductors.
For example: 208Y/120 3 phase 4 wire feeder for 500A continuous nonlinear load. Standard OCPD is 700A. Suppose you're using 90C Cu wire with 75C terminals. Then the minimum conductor size for the load (at 75?C terminal rating) is 1500MCM good for 625A. But with a current-carrying neutral, you have to derate the 90C ampacity of 705A for 4 conductors at 80% = 564A. So you increase the conductors to 2 parallel 500MCM in 2 pipes. The total derated ampacity is 688A and using the next larger size OCPD, it works.
So, you've increased the total ampacity but decreased the total CM's from 1,500,000 to 1,000,000.
The EGC required by Table 250-122 for a 700A OCPD is 1/0 Cu.
Do you increase the EGC from this and by what calculation?