A proposal ROP 2-166 was made by Mike Holt, that resulted in the CMP #2 adding a new exception to 210.19(A)(1) as follows:
" Exception No. 2: Grounded conductors that are not connected to an overcurrent device shall be permtted to be sized at 100 percent of the continuous and noncontinuous load.".
According to my view, that means a circuit with a continuous load of 80amps must use a breaker rated at 100amp and the ungrounded conductor has to be #3 CU rated at 100amp (based on 75C wire and breaker terminal requirements of 75C), both meeting the 125% coninuous load requirement.
The grounded neutral leg, however, only has to be sized at 100%, or 80amp. So, I can use #4 CU at 85amp capacity. What happens if the load malfunctions and the current goes up to 95amps? That's within the continuous range of the breaker and the ungrounded conductor, but 12% over the grounded conductor rating. WHAT KIND OF PROTECTED CIRCUIT IS THAT?
Please help an Engineer with only 37 limited years of experience understand.
" Exception No. 2: Grounded conductors that are not connected to an overcurrent device shall be permtted to be sized at 100 percent of the continuous and noncontinuous load.".
According to my view, that means a circuit with a continuous load of 80amps must use a breaker rated at 100amp and the ungrounded conductor has to be #3 CU rated at 100amp (based on 75C wire and breaker terminal requirements of 75C), both meeting the 125% coninuous load requirement.
The grounded neutral leg, however, only has to be sized at 100%, or 80amp. So, I can use #4 CU at 85amp capacity. What happens if the load malfunctions and the current goes up to 95amps? That's within the continuous range of the breaker and the ungrounded conductor, but 12% over the grounded conductor rating. WHAT KIND OF PROTECTED CIRCUIT IS THAT?
Please help an Engineer with only 37 limited years of experience understand.