Anyone see any problem with an installation of this sort:
 
_Existing_ sub-panel rated: 200 amp.
Actual current draw: 35 amps
New Feeder Conductors:#4
New Over current Device: 3 pole 70 amp breaker
 
I am presenting this question because I don't think there is anything wrong with the above. Some folks in this area say it's a "nameplate violation". The only possible reason that I can come up with for this thinking on their part is 110.3(A)7. But even here I feel it's not a violation since the feeder is ok for the load.
 
Anyone think differently?
Mike
	
		
			
		
		
	
				
			Anyone see any problem with an installation of this sort:
_Existing_ sub-panel rated: 200 amp.
Actual current draw: 35 amps
New Feeder Conductors:#4
New Over current Device: 3 pole 70 amp breaker
I am presenting this question because I don't think there is anything wrong with the above. Some folks in this area say it's a "nameplate violation". The only possible reason that I can come up with for this thinking on their part is 110.3(A)7. But even here I feel it's not a violation since the feeder is ok for the load.