250.64(B) Securing and Protection Against Physical Damage.
Where exposed, a grounding electrode conductor or its en-
closure shall be securely fastened to the surface on which it
is carried. Grounding electrode conductors shall be permit-
ted to be installed on or through framing members. A 4
AWG or larger copper or aluminum grounding electrode
conductor shall be protected if exposed to physical damage.
A 6 AWG grounding electrode conductor that is free from
exposure to physical damage shall be permitted to be run
along the surface of the building construction without metal
covering or protection if it is securely fastened to the con-
struction; otherwise, it shall be protected in rigid metal
conduit (RMC), intermediate metal conduit (IMC), rigid
polyvinyl chloride conduit (PVC), reinforced thermosetting
resin conduit (RTRC), electrical metallic tubing (EMT), or
cable armor. Grounding electrode conductors smaller than 6
AWG shall be protected in RMC, IMC, PVC, RTRC, EMT,
or cable armor