Per 240.4 (C), if the required ampacity of a conductor is over 800 amps, and if it does not match a standard rating for an overcurrent protection device, you must select the next lower rated device, not the next higher rated device.
But it appears to me that there is no similar rule for protecting the secondary of a transformer. For example, a 300 KVA transformer with a secondary voltage of 120/208V would have a rated secondary current of 833 amps. The maximum rating for the secondary protection device is 125% of this value, or 1042 amps. Despite the fact that this is more than 800, I am allowed to select the next higher rated device, and use a 1200 amp secondary breaker.
Am I reading this right? Is there something special about transformers that makes this a safe and acceptable practice?
But it appears to me that there is no similar rule for protecting the secondary of a transformer. For example, a 300 KVA transformer with a secondary voltage of 120/208V would have a rated secondary current of 833 amps. The maximum rating for the secondary protection device is 125% of this value, or 1042 amps. Despite the fact that this is more than 800, I am allowed to select the next higher rated device, and use a 1200 amp secondary breaker.