kamomeno68
Member
- Location
- Boulder, Colorado, United States
Here is my situation: NEC2014, Service conductors feed a meter, and then the meter feeds a typical panelboard. The meter housing and panelboard both have a 10kAIC rating. Let's assume the available fault current is 13kAIC at the input to the meter housing, and is 12.5kAIC at the input to the panelboard. Our local utility allows current-limiting fuses, which would dampen the available fault current below 10kAIC, to be installed on the line-side of the meter housing to provide protection from fault currents. The local AHJ is fine with this protection of the meter housing, but will not allow these current-limiting fuses to protect the panelboard. Even with the current-limiting fuses in place, the breakers in the panelboard are required to have kAIC ratings above 13kAIC. Can someone help me understand why? Are there any code references which support this paradigm? Thank you,
J
J