Protecting nm cables inside of emt

Status
Not open for further replies.

Max Headroom

Senior Member
Location
Claremont CA 91711
Occupation
General Building Contractor/Electrical Contractor
Hi everybody, If I use 3-4 ft of EMT to protect my exposed NM cable from the back of my panel up into the roof framing (four 12/2 nm inside of 4ft of 1 1/4 EMT) do I still need to derate for more than three ccc. The top of the conduit would have a bushing and the bottom end makes up into an LB (existing) which goes into the back of the panel. Total cross section area of the four cables, if I figured correctly, would be 1.097 in sq, and the emt is 1.496 in sq so about 73.33% fill. Thanks for any help,
 
Since it's merely a sleeve there is no fill calculation needed. You will need to derating being that it is over 24" but with 8 CCC's you're derated ampacity will be 21 amps.
 
Since it's merely a sleeve there is no fill calculation needed. You will need to derating being that it is over 24" but with 8 CCC's you're derated ampacity will be 21 amps.
OK I think I found it, Chapter 9 Table 1 Note 2, it infers we don't need to consider conduit fill for sections of conduit used to protect exposed wiring and cable from physical damage.
Thanks everyone, have a great day
 
Take a close look at 312.5(C) exception 1
OK so 312.5(C) Exception No. 1, this enclosure is in a wood box on the outside of the garage, inside the garage on the back of the cabinet is an existing LB which I had planned to use for convenience but according to exception 1
Exception No. 1:
Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure through one or more nonflexible raceways not less than 450 mm (18 in.) and not more than 3.0 m (10 ft) in length, provided all of the following conditions are met:
 
OK I have an idea I am going to move the EMT for him, it's running horizontally midway on a wall that he wants to cut a doorway into and it has the eight conductors mentioned earlier plus two 10awg on a dbl pole 30A, so I could move the EMT up and over the proposed doorway for the single pole circuits and then run some 10/3 mc for the double pole, problem solved
 
I figured that didn't apply.
I presume 312.5(C) applies anytime a cable type wiring method is entering a panel ?
I just remember that section becasue its like something I trip over then forget and proceed to trip over it again and again.
 
Take a close look at 312.5(C) exception 1
Are you referring to 312.5(C)(7) because if I am understanding that correctly then I would only be allowed 40% fill?

Where installed as conduit or tubing, the cable fill does not exceed the amount that would be permitted for complete conduit or tubing systems by Table 1 of Chapter 9 of this Code and all applicable notes thereto. Note 2 to the tables in Chapter 9 does not apply to this condition.
 
Are you referring to 312.5(C)(7) because if I am understanding that correctly then I would only be allowed 40% fill?

Where installed as conduit or tubing, the cable fill does not exceed the amount that would be permitted for complete conduit or tubing systems by Table 1 of Chapter 9 of this Code and all applicable notes thereto. Note 2 to the tables in Chapter 9 does not apply to this condition.
Yes and you mentioned a LB going into the back of the panel not top of the panel.
We have had some long threads on 312.5(C) Exception, I think I am a repeat offender, I have many times used flex as a sleeve for NM cable into a panel.
 
Yes and you mentioned a LB going into the back of the panel not top of the panel.
We have had some long threads on 312.5(C) Exception, I think I am a repeat offender, I have many times used flex as a sleeve for NM cable into a panel.
OK well this has definitely been good for me, the whole job was done years ago and is a mess, i just didn't want to add to the problem but now I have come up with a work around and I will not need to use NM cable, I'll probably use 3/4 EMT off the back of the cabinet for my 8ccc and then run a 10/3 mc for the one remaining 30A dbl pole circuit. Thank you all very much for your help!
 