Hi everybody, If I use 3-4 ft of EMT to protect my exposed NM cable from the back of my panel up into the roof framing (four 12/2 nm inside of 4ft of 1 1/4 EMT) do I still need to derate for more than three ccc. The top of the conduit would have a bushing and the bottom end makes up into an LB (existing) which goes into the back of the panel. Total cross section area of the four cables, if I figured correctly, would be 1.097 in sq, and the emt is 1.496 in sq so about 73.33% fill. Thanks for any help,