tonype
Senior Member
- Location
- New Jersey
I have never understood why it is required, but there is a required clear space of 6 feet above electrical equipment. Somewhere in 110. IIRC, the next paragraph exempts you from this requirement if you provide some kind of protection from condensation and leaks. Why it is Ok for pipes that are 6 feet above the equipment to leak but not 5.5 feet above it eludes me.
I would suggest that a drip tray under the piping is sufficient protection from leaks and condensation.
It would be also adequate IMO to provide equipment in drip proof enclosures. are those type 3R meter housings and switches?
are those type 3R meter housings and switches?
I'll bet the meter sockets are.are those type 3R meter housings and switches?
You can only use leak protection apparatus if the pipes are > 6' above the dedicated space. I can't remember when this dedicated space free of foreign system became code, but I think it was in the 2000's. Wonder if the install was compliant at the time, and now it is not? Sucks when they make a rule like that and you have all the equipment in an area you can no longer use -- makes service upgrades a major cost.
Don't see an exception for 3R equipment, but it seems like it would be a reasonable exception.
A structural ceiling between the pipes and equipment would most likely spread out the leak to a much wider area and who knows where it would eventually drip down.
110.26(E) Dedicated Equipment Space. All switchboards, pan-
elboards, and motor control centers shall be located in dedi-
cated spaces and protected from damage.
The dedicated electrical space, which extends the footprint
of the switchboard or panelboard from the floor to a height
of 6 ft above the height of the equipment or to the structural
ceiling (whichever is lower), is required to be clear of pip-
ing, ducts, leak protection apparatus, or equipment foreign
to the electrical installation. Plumbing, heating, ventilation,
and air-conditioning piping, ducts, and equipment must be
installed outside the width and depth zone. Busways, con-
duits, raceways, and cables are permitted to enter equipment
through this zone.
Foreign systems installed directly above the dedicated
space reserved for electrical equipment are required to
include protective equipment that ensures that occurrences
such as leaks, condensation, and even breaks do not damage
the electrical equipment located below.
Sprinkler protection is permitted for the dedicated
spaces as long as the sprinkler or other suppression system
piping complies with 110.26(E)(1)(c). A dropped, sus-
pended, or similar ceiling is permitted to be located directly
in the dedicated space, as are they are not considered struc-
tural ceilings. Building structural members are also permit-
ted in this space.
I'll bet the meter sockets are.
The EMT set screw fittings and no sealing hub kills that though.