We are replacing an existing motor, its controller, and the mechanical components driven by the motor. “We” (i.e., my group, but long before I started work here) gave the Contractor a schematic diagram of what is to go inside the controller. The Contractor will build this thing. So right off the bat I don’t see a UL listing being given, but I don’t think that is an issue. Here is my issue: There is a 50 amp breaker in the upstream distribution panel.
There is a 50 amp “motor circuit protector” as the first component inside the controller.
We told the Contractor to run #10 wires from the controller to the motor. It is a 5HP, 208V, 3 phase motor – 16.7 FLA). I think that is OK.
However, upstream of the #10 wires the only OCPD is set at 50 amps.
Article 430 has never been a friend of mine. Is this OK? Is there something I should look for in our specifications and/or the Contractor’s submittal to verify that some other protective device is included?
FWIW, the motor will likely be run only for periodic testing, perhaps four times a year. Each time, however, it will run for about 45 minutes before it is stopped.
There is a 50 amp “motor circuit protector” as the first component inside the controller.
We told the Contractor to run #10 wires from the controller to the motor. It is a 5HP, 208V, 3 phase motor – 16.7 FLA). I think that is OK.
However, upstream of the #10 wires the only OCPD is set at 50 amps.
Article 430 has never been a friend of mine. Is this OK? Is there something I should look for in our specifications and/or the Contractor’s submittal to verify that some other protective device is included?
FWIW, the motor will likely be run only for periodic testing, perhaps four times a year. Each time, however, it will run for about 45 minutes before it is stopped.