natfuelbill

Senior Member
What is the Standard that requires the design and construction of an enclosure to protect against someone inserting a rod through a ventialtion opening (or some other opening) and into the enclosure?

Happy T-day!!!
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
natfuelbill said:
What is the Standard that requires the design and construction of an enclosure to protect against someone inserting a rod through a ventialtion opening (or some other opening) and into the enclosure?

Happy T-day!!!

Some sources are:
UL/NEMA Type 1 enclosures
NFPA 79
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
natfuelbill said:
What is the Standard that requires the design and construction of an enclosure to protect against someone inserting a rod through a ventialtion opening (or some other opening) and into the enclosure?

Happy T-day!!!

NEMA/UL type 1 enclosures do this. It is not a requirement to use such an enclosure AFAIK.
 