In article 230.50 (B)(1) list what can be use to protect service - entrance cables entering the house. Number 6 is other approved means. Would sealite ( LFNC ) be one of those approved means?
Note that 230.50 is concerned with service conductor subject to physical damage. If they are not subject to damage, 230.43 would be applicable and it allows LFNC.