I have an old office where the protection for two air conditioners is questionable. The air conditioners help to reduce the temperature of a computing system installed into a small cabinet. There is no much room in the cabinet for additional equipment. These air conditioners don't have independent protection, but they both are connected to a terminal strip and the terminal strip is connected to a 20 A two pole 120/240 breaker. The length between the terminal strip and the breaker in the panel board is 12 feet. I normally see each air conditioner unit with its own individual max breaker and disconnect. They are having air conditioner issues so professionals are already going to be recommended. I would appreciate others insight and opinion as to this situation. Thank you
Background: The air conditioner units are installed on each door of the cabinet. Each unit has internally a 15 A class T fuse, works at 208 VAC phase-phase, but it is rated to work at 230 VAC on the label, and the load is: 5 A nominal current and 10 A starting current. Wiring conductor is # 12 AWG THHN/THWN copper stranded.
Background: The air conditioner units are installed on each door of the cabinet. Each unit has internally a 15 A class T fuse, works at 208 VAC phase-phase, but it is rated to work at 230 VAC on the label, and the load is: 5 A nominal current and 10 A starting current. Wiring conductor is # 12 AWG THHN/THWN copper stranded.