I had an inspector tell me that Sch 80 PVC was required for anything from 18" below grade up to 8'. His reference was 300.5
I told him I didn't think that was right and would look it up. 300.5(D)(1) says basically what he said but that is for protection of direct buried conductors emerging from below grade and doesn't mention Sch80.
The other reference that I was able to find was 300.50(C) but that is for over 1000V
I know all the "subject to physical damage" stuff is subject to interpretation. I'm just talking about specific language as to Sch 80 being required up to 8'.
I told him I didn't think that was right and would look it up. 300.5(D)(1) says basically what he said but that is for protection of direct buried conductors emerging from below grade and doesn't mention Sch80.
The other reference that I was able to find was 300.50(C) but that is for over 1000V
I know all the "subject to physical damage" stuff is subject to interpretation. I'm just talking about specific language as to Sch 80 being required up to 8'.