vpower1989
- USA
- Engineer
I am running into a situation where a piece of equipment came in with an FLA listed on the nameplate that is higher than we were anticipating. We were told to provide a 30A circuit with a L21-30R. #10 conductors have been installed. The equipment shows up and we have an FLA of 25.14A listed on the nameplate. The electricians are asking if they need to pull a new 40A circuit. So I have been going down the rabbit hole of splitting hairs to see if we can use the #10s.
So in my mind the ampacity of conductors are fine for the load. I may have to ditch the RCPT and go to a disconnect. One question I have is on the "next size up" rule. Could I protect the conductors described above with a 40A breaker?
- So nameplate FLA is 25.14A, we treat it as a continuous load, 25.14 * 1.25 = 31.4A required rating for the conductors
- We likely have 75C terminations, #10 is rated for up to 35A.
- No temperature adjustments required.
- Conduit Derating – 90C cable (THHN) – 40A * derating factor ( .8) = 32A.