I really don't know how to read these settings, but it appears to me that this relay will send the trip signal when the current exceeds 800 amps. Is that correct?
Manufacturer:
GE​
Model (Type):
12IAC51B806A​
Style (Cat.#):
N/A​
Delay Unit Range:
2 – 16 Amps​
Instantaneous Range:
10 – 80 Amps​
CT Ratio:
400/5​
TC Characteristic:
Inverse​
Instruction Publication:
GEK-34053​
Delay Unit P/U (tap):
10A​
Time Dial:
3​
Instantaneous P/U**:
60A​
 
Not enough information.
The data provided simply sets up the curve of the device and its Inst pickup of 12X (in your case 4800A).

You need to find some logic for each of its output contacts.
 
I really don't know how to read these settings, but it appears to me that this relay will send the trip signal when the current exceeds 800 amps. Is that correct?
Manufacturer:
GE​
Model (Type):
12IAC51B806A​
Style (Cat.#):
N/A​
Delay Unit Range:
2 – 16 Amps​
Instantaneous Range:
10 – 80 Amps​
CT Ratio:
400/5​
TC Characteristic:
Inverse​
Instruction Publication:
GEK-34053​
Delay Unit P/U (tap):
10A​
Time Dial:
3​
Instantaneous P/U**:
60A​
34 page manual
 
Two trip elements - inverse time delay and instantaneous. 400/5 CT is 80:1 The time delay unit (51) picks up at 10 A secondary or 800 A primary. The instantaneous unit trips at 60 A secondary or 4800 A primary with no (intentional) time delay.
 
I was just looking for the trip setting to look at adding additional load to the 5kV circuit but the ungerground conductors are only 350 kcmil, so this really doesn't help.
I will see if I can get the actual load data for their process control system and work from that.
 
I was just looking for the trip setting to look at adding additional load to the 5kV circuit but the ungerground conductors are only 350 kcmil, so this really doesn't help.
I will see if I can get the actual load data for their process control system and work from that.
Remember that MV feeders are often sized for short circuit protection and not overload
 