DBoone
- Mississippi
- General Contractor
It doesn't appear to me that the equipment grounds are spliced with a device identified for the use. Also I don't see EGC pigtails for the switches.
How many wires are installed in the wire nuts? They appear to be Ideal Tan wirenuts.
Chris
Why do my pictures from my iPhone appear sideways on the forum?
171229-2429 EST
If you compare an insulator of thickness T that is composed of one solid layer vs the same material applied in many thinner layers, then you will find the long term voltage breakdown to be better with the multilayer construction.
171230-1225 EST
GoldDigger:
When insulators are produced, like enameled wire, there are very small imperfections existent or produced that have a different dielectric constants than the insulating material itself. When a voltage is applied to the insulator these imperfections may have a resulting higher field intensity resulting in an electrical discharge, heat, and destruction of adjacent insulating material. These pockets tend to grow.
By applying the insulation in layers the interface between layers tends to reduce the propagation of these breakdown spots. These breakdow pockets can be seen with a microscope. There is no semiconductor layer applied. But it does bring up the point that if conductive layers were at these interface layers could there be a further improvement.
I believe that thinner sections of insulating material have a greater breakdown voltage gradient.
Wire insulation for electric or hybrid car motors is being made with about 10 to 15 very thin enamel layers.
At the old GMI, now Kettering University, they are performming tests on various insulators in their high voltage lab.
171230-1437 EST
mbrooke:
If you place a 1 micron, about 0.000,04", layer of enamel on a wire, and continue to add 15 similar layers, then total thickness is about 0.000,6".
At 2000 V/mil the breakdown would be about 1200 V.
171230-1930 EST
mbrooke:
If you had used one single layer of enamel 0.000,6" thick the breakdown might have been only 1500 V/mil or about 900 V for the total thickness of 0.000,6".
This general concept is from reading and presentations. I have not directly run the experiments.
General Motors is using magnet wire with layered enamel in production electric vehicles to improve motor power to weight ratio, and improve reliability. I suspect everyone is doing the same.
In general an insulator has a higher breakdown voltage for a short duration, but there will be a gradual decline in breakdown as exposures increase in duration, and/or total exposure time increases.
171231-0951 EST
mbrooke:
If you take a fixed space (thickness) and fill it solid with an insulating material and measure the breakdown voltage, then change to filling this same space with multiple layers of the same material the breakdown voltage will increase. The increase in breakdown over a short time, or in the lifetime of adequate breakdown is apparently worth the extra work in some applications. Ordinary electrical work probably not.
The tensile strength, #/sq-in, of glass increases as the diameter is reduced. A similar characteristic.