Have a yard with some conex boxes and owner wants to supply power to each, multiple receptacles mounted on exterior etc. no power on the interior. Had a couple red flags in my head.
1. 225.30, I would think each box would be a 'structure' and therefore since we need multiple circuits, both 120 and 240, each box has to have a load center so that it can be supplied by a single feeder and meet this requirement.
2. Grounding. An equipment grounding conductor will go to the load center on the box from the SES, but then what about the box itself? Would you just bond to the equipment ground bar in load center attached the the box, or need some grounding electrode system for the structure itself?
Any other issues with this I'm not thinking of?
1. 225.30, I would think each box would be a 'structure' and therefore since we need multiple circuits, both 120 and 240, each box has to have a load center so that it can be supplied by a single feeder and meet this requirement.
2. Grounding. An equipment grounding conductor will go to the load center on the box from the SES, but then what about the box itself? Would you just bond to the equipment ground bar in load center attached the the box, or need some grounding electrode system for the structure itself?
Any other issues with this I'm not thinking of?