provisions for grounding TV/TELE to electric system

Status
Not open for further replies.
for sake of argument I have two ground rods driven properly spaced, I am using #4 grounding conductor. I have provided 12 inches of this #4 conductor at the ground rod for the CATV and Tel Co to connect to, am I correct in doing this I can't seem to find any reference to this method, I just seem to remember seeing an illustration or reading it some where.

Thanks Roy
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: provisions for grounding TV/TELE to electric system

It complies with 800 and 820 as long as the grounding conductor from the CATV and Telco are at least a #14 AWG and not longer than 20 feet to the connection on the GEC you mentioned.
 