chris kennedy said:
What is PT? There should be no terminations for you to make in a CT can other than bonding. Your conductors should pass straight through POCO's CT's into your MDP.
PT = Potential (or voltage) Transformer.
Remember, power is a measure of both voltage and current; all watt and watt-hour meters must have a way of sensing both. The voltage can either be directly fed into the meter, or stepped down through a transformer.
The typical 3-phase CT setup has three current circuits and three voltage circuits, all of which share a single neutral conductor. So, there are seven conductors (usually #10) in the 1-1/4" conduit we provide.
As long as the meter is calibrated to convert the representative current and voltage into actual full current and voltage readings, it will read out in actual power over time (watt-hours).
CT's are basically step-up voltage transformers, with the "primary" a single winding (the conductor or bar) and the secondary the number of turns it takes for the application; for example 400:5 is 80 "secondary" turns.
By effectively shorting the secondary with the ammeter portion of the watt meter, the high voltage is instead converted into amps. For every 80 service amps, one amp will flow in the meter circuit.
Without the low-impedance ammeter, or shorting bars for meter removal, the CT would indeed behave as a step-up transformer, and could reach thousands of volts open-circuit, damaging the insulation inside the CT.