buildings heating and cooling so only one small fan 65W each roomCould you elaborate further.
What is the load. I would be it is greater than 65w
buildings heating and cooling so only one small fan 65W each room
Still don't get it.
PTAC's generally draw more current than that.
are speaking of a fan coil?
I would say a fan coil 65 watts could be powered by a general branch circuit other than a kitchen appliance, Laundry or bathroom circuit.
Still don't get it.
PTAC's generally draw more current than that.
are speaking of a fan coil?
I would say a fan coil 65 watts could be powered by a general branch circuit other than a kitchen appliance, Laundry or bathroom circuit.
Guessing the heating is provided by a hot water system/boiler or NG, the cooling by refrigerant lines from a 'master' AC unit, and the PTAC is just the thermostat and blower for airflow. But that isnt a PTAC to me
prudent, what do the mfg specs call for? A 65W load shouldnt require a dedicated circuit. Is there any chance a true PTAC, with integral compressor (and possibly back-up heating coils) would be installed in the future? a 9k BTUunit of that type draws about 7A on a 240V line, 15k BTU about 12, with backup heat going up to around 15-16A.
210.52
(I) Outlet Requirements For Re
sidential-Type Occupancies.
In addition to the requirements set forth in subsections (A) through (H) of this section, living rooms, bedrooms, dining rooms or similar rooms shall have at least one receptacle outlet installed for air conditioners. Such outlets shall be supplied by an individual branch circuit.
Exception: Buildings with central air conditioning systems that serve any of the above areas shall not require separate outlets in those areas.