I was sent data by a transformer manufacturer
since this is used in an XP piece of equipment we do fault calcs to determine let thru energy based on fusing
transformer
12470/240/1
15 kva
they state PU Z 5.12%
prim test V 638.8 V
prim test I 1.2 A
so 638.8/12470 = 5.12%, X/R = 4.11/3.06
doesn't sound right when compared to standard tables, they state 1.8% for this xfrm
they also give the actual measured R for the prim and sec:
prim 128.641 Ohm
sec 0.02572 Ohm
when I calculate the PU act/base for the prim or sec I get 1.9% (close to the standard tables)
eg, Z prim = (128.641 + (12470/240)^2 x 0.02572) / (12470^2/15000) x 100 = 1.91%
what do you guys come up with based on the measured R?
big difference in I fault 5.12 vs 1.9
I have an email into the mfg