I apologize if this is in the wrong forum.I have recently found a Public Utility Company that is in direct violation of the NEC when connecting to a meter bank without using an oxidant inhibitor on any of it's aluminum wiring. Is there any recourse that I have as an inspector? I have not been approving the meter installation until this has been corrected, yet it is causing an uproar? Any help?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: Public Utility Companies

This is probably the right place to post your question. We are going to have to hope that "The Other Charlie" or another utility person can answer this one for you. But my initial reaction is that the NEC does not apply to a public utility. They are governed by their own rules. So the question would become, "Are they following their own rules?" and not "Are they following the NEC?"
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Public Utility Companies

Originally posted by USMCRecon:
I apologize if this is in the wrong forum.I have recently found a Public Utility Company that is in direct violation of the NEC when connecting to a meter bank without using an oxidant inhibitor on any of it's aluminum wiring. Is there any recourse that I have as an inspector? I have not been approving the meter installation until this has been corrected, yet it is causing an uproar? Any help?
Most public utilities work under the NESC not the NEC.

The NEC does not require oxidant inhibitors on aluminum conductors.

Unless the manufacturer requires it.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Public Utility Companies

There is also article "90.2(B)(5)a" that takes this out of the NEC.