Tom is right, 314.28 puts requirements for 4AWG or larger, to ensure the JBs have enough volume.
Often violated is 314.28(A)(2)
"The distance between the raceway entries enclosing the same conductors shall not be less than six times the metric designator (trade size) of the larger raceway."
Also see 300.34 Conductor bending radius.
Russ