Pull and Junction Boxes and Conduit Bodies

Status
Not open for further replies.

dpenbert

Member
Location
Missouri
How does one size a pull box that contains one angled pull and two straight pulls, where all three raceways contain conductors 4 AWG or larger?
 
Re: Pull and Junction Boxes and Conduit Bodies

Hello,

I see that for angled pulls you multiply 6 times the largest raceway and for straight pulls you multiply 8 times the largest raceway. I have both types of pulls going into the pull box, so your saying I need to multiply the largest raceway by 6 and ignore the requirement for straight pulls?

Thanks
 
Re: Pull and Junction Boxes and Conduit Bodies

Do both calculations and use whichever results in the greater dimensions.

Ed
 
Status
Not open for further replies.
Top