Looking for some confirmation on a design:
I have a below-grade conduit duct bank from Pull Box #1 to another Pull Box #2 (Approx. 150'). Pull Box #1 is located in an unclassified area. Pull Box #2 will be in a Class I, Div. 2 rated building. I plan on running PVC Conduit between the pull boxes in a concrete-encased duct bank 24" below grade. Reading the Code I believe this is acceptable however I will need to transition to Rigid Conduit for the last 24" of the underground run to the emergence of Pull Box #2 (Since it is located in the Class I, Div. 2 area). Conduit seals would be required at the stub-up location in Pull-Box #2. A standard NEMA 1 enclosure would be acceptable for Pull Box #2. Is my code interpretation correct? I appreciate any help you can provide!
I have a below-grade conduit duct bank from Pull Box #1 to another Pull Box #2 (Approx. 150'). Pull Box #1 is located in an unclassified area. Pull Box #2 will be in a Class I, Div. 2 rated building. I plan on running PVC Conduit between the pull boxes in a concrete-encased duct bank 24" below grade. Reading the Code I believe this is acceptable however I will need to transition to Rigid Conduit for the last 24" of the underground run to the emergence of Pull Box #2 (Since it is located in the Class I, Div. 2 area). Conduit seals would be required at the stub-up location in Pull-Box #2. A standard NEMA 1 enclosure would be acceptable for Pull Box #2. Is my code interpretation correct? I appreciate any help you can provide!