Underground primary conduit run to utility transformer when it turns, is a pull box required?
A anbm Senior Member Location TX Occupation Designer Aug 17, 2016 #1 Underground primary conduit run to utility transformer when it turns, is a pull box required?
iwire Moderator Staff member Location Massachusetts Aug 18, 2016 #2 anbm said: Underground primary conduit run to utility transformer when it turns, is a pull box required? Click to expand... As far as the NEC only if you exceed 360 degrees of bends without one. But the utility may have requirements for one.