What is the maximum conduit run before you have to install a pull box?
Thanks
Gene
Thanks
Gene
Gene Shults said:What is the maximum conduit run before you have to install a pull box?
kingpb said:Pulling tension and side wall pressure calculations need to be done to determine maximum length of a specific conductor pull so that cable damage does not occur.
cloudymacleod said:ummm. some workers have a rule of thumb of ever 100' put a pull box as long there aint no more than 360 degrees in the bends
kingpb said:Pulling tension and side wall pressure calculations need to be done to determine maximum length of a specific conductor pull so that cable damage does not occur.![]()
The 360 rule is for number of bends and does not determine an acceptable length of run.
i.e. if the run is long enough, simply having 1 x 90 deg bend could cause cable damage on the pull.
dlhoule said:How much side wall pressure is there on a 200' vertical pull?![]()
dlhoule said:How much side wall pressure is there on a 200' vertical pull?![]()
Trevor What would be the difference between a 500 ft vertical pull like from vault to vault ,as compared to a 500 ft pull from a sweep into a trans and going into a M.D.P.The only difference is the sweeps ??????????infinity said:Vertical pulls present a completely different set of rules. Conductors are required to be supported. If you have a 500' straight vertical pipe run and pull in 500 Kcmil conductors you'll need a pull box every 50' to support the conductors.
allenwayne said:Trevor What would be the difference between a 500 ft vertical pull like from vault to vault ,as compared to a 500 ft pull from a sweep into a trans and going into a M.D.P.The only difference is the sweeps ??????????
hillbilly said:Enough to make your fundament bulge out.
steve
iwire said:The difference is that the vertical one (up and down) is required to be supported and the horizontal one (sideways) is self supporting.