A picture is worth a 1000 words so I will shut up.

ry%3D400
 
If you look at the Exception to 314.28(A)(2), it will refer you to Table 312.6(A) when your conduits enter opposite to a removable cover.
In you case, I believe that dimension is 4".
 
No matter which or what set of rules you use ,you still must comply with

2008 ,,,,, 300.34 (conductor bending radius) that comes to the front often.

dick
 
No matter which or what set of rules you use ,you still must comply with

2008 ,,,,, 300.34 (conductor bending radius) that comes to the front often.

dick

I disagree. Art. 314.28(A)(2) clearly states to use 312.6(A). IMO that overrides 300.34
 
Off the top of my head, we may be mixing apples and oranges.
300.34 references cables over 600 volt. Although I don't notice a voltage limitation on 314.28, there is a separate section for cables over 600v (314.70 & .71) which does reference 300.34
 