I have 3 4 inch conduits on each side of my box it is going to be a angle pull there is a total of 6 conduits they all will have 3 400 mcm and a 2/0 ground what size will my pull box be
I have 3 4 inch conduits on each side of my box it is going to be a angle pull there is a total of 6 conduits they all will have 3 400 mcm and a 2/0 ground what size will my pull box be
Can you show us how you arrived at that number ?
(there are many folks here that can give you the answer, but it's important for you to know how to obtain it)
Good start, but off a bit.
Your Code reference is 314,28
For angle pulls your basic rule is 6 X the conduit diameter, so we start with 6 x 4 = 24
To that you add the sum of the diameters of conduits in the same row...if your other 2 conduits are in the same row thats an adder of 8" for a total of 32".
This would be true for the two sides opposing the entries,
In this case, since you have nothing coming in the back, the depth would be what is needed for your conduits.
My guess would be a 32 x 32 x 6 or 8
There are a couple of other important conduit location measurements so please review 314.28
I have 3 4 inch conduits on each side of my box it is going to be a angle pull there is a total of 6 conduits they all will have 3 400 mcm and a 2/0 ground what size will my pull box be
How about trying to answer it yourself and then we will help.
Can you show us how you arrived at that number ?
(there are many folks here that can give you the answer, but it's important for you to know how to obtain it)
Good start, but off a bit.
Your Code reference is 314,28
For angle pulls your basic rule is 6 X the conduit diameter, so we start with 6 x 4 = 24
To that you add the sum of the diameters of conduits in the same row...if your other 2 conduits are in the same row thats an adder of 8" for a total of 32".
This would be true for the two sides opposing the entries,
In this case, since you have nothing coming in the back, the depth would be what is needed for your conduits.
My guess would be a 32 x 32 x 6 or 8
There are a couple of other important conduit location measurements so please review 314.28
What did I miss between post #1 and #4? Seems there was some other posts from OP that aren't shown according to some of the questions asked back to him.
Maybe I'm blind or just slow, but something is confusing about this to me!:?
I was wondering about that too. At first I thought of PM, but that did not make sense to reply to publicly without quoting, Then I though that perhaps the OP started the thread as a Moderated Member, and the Moderators could see posts that we did not see yet?
I was wondering about that too. At first I thought of PM, but that did not make sense to reply to publicly without quoting, Then I though that perhaps the OP started the thread as a Moderated Member, and the Moderators could see posts that we did not see yet?
I must confess that I saw them before I made that guess. :ashamed1:Winner!
The missing posts are now showing!
I think Jumper accidentally deleted 2 posts instead of one. I undeleted one.Winner!
The missing posts are now showing!
I think Jumper accidentally deleted 2 posts instead of one. I undeleted one.
Okay.... fine, just don't hurt him.Ban Jumper!![]()