Pull box sizing

Status
Not open for further replies.

Nslater

Member
Location
Tampa
Occupation
Inspector
Question about pull box sizing. If I have a wall of a box with angled and straight pulls the largest conduit being the straight pull. I know that for straights we would use the x 8 method. My question is for the angled pull calculation we are supposed to use the largest pipe x 6 plus the sum of other conduits. If the largest conduit is a straight pull do we use that conduit x 6 OR the largest angled pull conduit? Then the sum of the remaining conduits which would include the larger straight pull conduit.
 
From what I understand each wall in the box must be calculated on it's own. So I would say the straight pull conduit would be included in the calculation if it enter the box on the same side as the angle pull conduits
 
I think I figured that out today with some other people at work. What we “think” largest pipe x6 even if it’s not an angels pull then the sum of the others. You agree?
 
Status
Not open for further replies.
Top