While on an inspection I wrote up a 6x6 box with an 1 1/2" conduit running in the top and out the bottom (straight pull 314.28.A.1 8 times) the box should be 12".
I understand the box should be sized for the conductors.
There were several conductors running through the conduit all low voltage, one of the low voltage conductors was about the size of a 4/0 the others about the size of a # 8 or smaller.
When the engineer read my report he called and said that this article only applies to power not low voltage. I on the otherhand believe it applies to everything.
Have I been wrong all these years.