Can someone help me with this new installation. The contractor install this maybe 16”x16” surge protection termination box and used it as a pull box as well. It has one 4” and one 2” conduit in bottom and four 2” out the top. There are 3 larger 1.5” multi-conductor cables and multiple little ones. Some passing straight through and others are connected to the surge devices. Can someone tell me the code for pull box sizing for control cables? This to me just doesn’t seem right. To me it a surge device panel not a pull box. Thanks.
Please let me know if further info is needed.
Voltage is 24VDC, 4-20ma some analog and digital circuits
Please let me know if further info is needed.
Voltage is 24VDC, 4-20ma some analog and digital circuits