In most states you have to know how to size one correctly in order to get an electrical contractors license. As a designer, you know there is a foot note at the bottom of the blue prints stating everything should be done by the NEC. So if we (electricians) happen to catch one on the prints that is to small we can get a bigger one.Is pull box typically sized by contractor? i.e. underground or overhead pull box for large conduits (6 - 8 of 4"C)
hit and turn...
For a large job where the conduit runs are designed by the engineer we typically would have our own shop drawings with the box sizes. Otherwise the guys in the field size the junction boxes. I would prefer to size my own. Often the penny pinchers use the 8X calculation to size the boxes and they're too small.Is pull box typically sized by contractor? i.e. underground or overhead pull box for large conduits (6 - 8 of 4"C)
hit and turn...
We might see them on bid drawings but the size isn't on there.hi - EE here. Doing retail CDs. I never put pullbox or JB sizes on drawings. Don't want to get in the way of the EC's methodology.
Enough that you can install the locknuts and bushings.I saw NEC has rule to size box vertical and horizontal dimension, what's about box height? any rules?
Same here. That is means and methods. Hardly ever see a contractor run the conduits exactly as shown on plans. If the entry and exits change because of the way the EC wants or needs to run the conduits or sizing could be wrong.hi - EE here. Doing retail CDs. I never put pullbox or JB sizes on drawings. Don't want to get in the way of the EC's methodology.