ohmhead
Senior Member
- Location
- ORLANDO FLA
I have a question about pull boxes article 314# straight pulls are eight times the largest raceway which is the length of the box .
Angle or U- pull is six times the largest raceway plus increased for additional entries in that same row .
What if you come into the back of a large pull box and exit the sides is it still covered by the NEC because its not explained that way in the code book . Code only shows side wall to opposite side wall it does not express back wall .
So were not using the side wall we are coming into the back of the box with 8# 3" conduits and exiting the pull box on both sides 4 conduits on the left side and four on the right side .
Would bending radius 300.34 take over this requirement .
Reason iam asking is one inspector says yes its not in the code and its fine .
Now we have a new inspector which says no it needs to be per the code but my question to him was show me were it explains back wall to side wall .
As long as we have the bending space should we be ok with 300.34 ?
Which inspector is correct ?
Angle or U- pull is six times the largest raceway plus increased for additional entries in that same row .
What if you come into the back of a large pull box and exit the sides is it still covered by the NEC because its not explained that way in the code book . Code only shows side wall to opposite side wall it does not express back wall .
So were not using the side wall we are coming into the back of the box with 8# 3" conduits and exiting the pull box on both sides 4 conduits on the left side and four on the right side .
Would bending radius 300.34 take over this requirement .
Reason iam asking is one inspector says yes its not in the code and its fine .
Now we have a new inspector which says no it needs to be per the code but my question to him was show me were it explains back wall to side wall .
As long as we have the bending space should we be ok with 300.34 ?
Which inspector is correct ?