I’m reviewing a large pull box Construction wants to install. The proposed box is 30”W x 36”H x 12”D. There are two feeders involved: both are 600kCMIL; 3 per ph with a full sized neutral and #1/0EGC. The conduits are 3.5” each, RGS - 6 total.
The conduits will penetrate a wall and enter the back of the Box, then exit the left side (looking at the front) The box appears long & wide enough to meet 314.28, but I’m a little concerned about the depth. It has a hinged door opposite the wall penetrations which seems to make this box acceptable as far as intent. Cable is single conductor, 600V insulation, XHHW-2 approximately 1 inch OD which according to 336.24 makes the bend radius around 5 inches. Any comments?
Sent from my iPhone using Tapatalk
The conduits will penetrate a wall and enter the back of the Box, then exit the left side (looking at the front) The box appears long & wide enough to meet 314.28, but I’m a little concerned about the depth. It has a hinged door opposite the wall penetrations which seems to make this box acceptable as far as intent. Cable is single conductor, 600V insulation, XHHW-2 approximately 1 inch OD which according to 336.24 makes the bend radius around 5 inches. Any comments?