That's what I was thinking... also was wondering maybe the "pullbox" isn't really a pullbox in this scenario. Maybe the pullbox is considered a larger wireway? This is such a gray area...I would do like you do for cables...translate to conduit size.. Look at the conductors in the wireway, and find the smallest conduit size that those conductors will fit in and use that conduit size for you box size calculations. However the code does not say that.
what if I have conduits coming out of the wireway instead of the pullbox? Does the conduits coming out of the wireway need to follow angle pulls?I would do like you do for cables...translate to conduit size.. Look at the conductors in the wireway, and find the smallest conduit size that those conductors will fit in and use that conduit size for you box size calculations. However the code does not say that.
See 376.23(B). Note that it works a bit different than the pull box rules, as you only need to comply with the distance between conduit entries for the wireway.what if I have conduits coming out of the wireway instead of the pullbox? Does the conduits coming out of the wireway need to follow angle pulls?