I have an installation where (3) 4" EMT conduits will be entering a pullbox from the bottom, and exiting out the back (at the top)
Assuming that I'm correct that since the conductors don't exit directly across from each other, the calculation would be (6x4")+4"+4" = 32" so a 32" x 32" box.
My real question is concerning the depth of the pullbox. Do I use Table 312.6(A) to calculate the depth? I am installing (4) 400kCMIL, so I see that as 12". Is that correct?
My next concerns is that I read an article by Mike Holt in EC&M (http://www.ecmweb.com/code-basics/sizing-junction-boxes) and he indicates that when conductors enter an enclosure with a removable cover, the distance from the removable cover to where the conductors enter must mot be less that the bending radius listed in Table 312.6(A) based on one conductor per terminal. So 6" should be deep enough?
The size of my pullbox should be 32"x32"x6" correct?
Assuming that I'm correct that since the conductors don't exit directly across from each other, the calculation would be (6x4")+4"+4" = 32" so a 32" x 32" box.
My real question is concerning the depth of the pullbox. Do I use Table 312.6(A) to calculate the depth? I am installing (4) 400kCMIL, so I see that as 12". Is that correct?
My next concerns is that I read an article by Mike Holt in EC&M (http://www.ecmweb.com/code-basics/sizing-junction-boxes) and he indicates that when conductors enter an enclosure with a removable cover, the distance from the removable cover to where the conductors enter must mot be less that the bending radius listed in Table 312.6(A) based on one conductor per terminal. So 6" should be deep enough?
The size of my pullbox should be 32"x32"x6" correct?