I thought # 12 NM was rated for 25 amps, why cant I use it for 23 amps . for a/c unite .
Maximum 20A OCPD, though..... Use MC or conduit and wire and you're good with #12 which is 25 amps @75° C.
Yet another AC question.
Unit minimum amps 23.
Using nm cable.
Is the rating taken from the 90 degree because of thhn or 60 degree because it's nm ?
Thank you
60° so #10 is required for NM cable. Use MC or conduit and wire and you're good with #12 which is 25 amps @75° C.
In the context of this discussion, yes. 240.4(D) allows the small conductor rule to be ignored for motors and air conditioners.So is this correct??? #12 wire in conduit is good for 25A @ 75 degC???
So is this correct??? #12 wire in conduit is good for 25A @ 75 degC???
Yes that is true. However number 12 wire is limited to a 20A OCPD (excluding motor circuits see 430.52, or welders see 630.12, or A/C see 440.22, etc etc see 240.4(G)). The 25 amps is useful for derating purposes. In that case it is good to 30A at 90C. The 25/30A is good for not more than 3 current carrying conductors in the raceway. Above that and you must start derating. Also you must derate for ambient temperatures above 30C (see 310.15)