Pulled 10's where 12's were sufficient?

Status
Not open for further replies.

ritelec

Senior Member
Location
Jersey
Yet another AC question.

Unit minimum amps 23.

Using nm cable.

Is the rating taken from the 90 degree because of thhn or 60 degree because it's nm ?

Thank you
 
60° so #10 is required for NM cable. Use MC or conduit and wire and you're good with #12 which is 25 amps @75° C.
 
NM

NM

I thought # 12 NM was rated for 25 amps, why cant I use it for 23 amps . for a/c unite .
 
Yet another AC question.

Unit minimum amps 23.

Using nm cable.

Is the rating taken from the 90 degree because of thhn or 60 degree because it's nm ?

Thank you

NM cable ("romex") is a special case where the 60C column of the NEC limits the ampacity prior to bundling and ambient calculations, no matter what the temperature ratings of the equipment terminations and wire/cable may be. This is specific to NM cable per 334.80.
 
So is this correct??? #12 wire in conduit is good for 25A @ 75 degC???

Yes that is true. However number 12 wire is limited to a 20A OCPD (excluding motor circuits see 430.52, or welders see 630.12, or A/C see 440.22, etc etc see 240.4(G)). The 25 amps is useful for derating purposes. In that case it is good to 30A at 90C. The 25/30A is good for not more than 3 current carrying conductors in the raceway. Above that and you must start derating. Also you must derate for ambient temperatures above 30C (see 310.15)
 
Yes that is true. However number 12 wire is limited to a 20A OCPD (excluding motor circuits see 430.52, or welders see 630.12, or A/C see 440.22, etc etc see 240.4(G)). The 25 amps is useful for derating purposes. In that case it is good to 30A at 90C. The 25/30A is good for not more than 3 current carrying conductors in the raceway. Above that and you must start derating. Also you must derate for ambient temperatures above 30C (see 310.15)

Is the neutral in a MWBC in metallic conduit with 4 wires (3 phases A,B,C and a neutral) considered a CCC???? It should not be IMHO!!!!! What is the max allowed in this case. Can I use 8 as opposed to 6 650 kVA/277VAC fixtures per cct????
 
Is the neutral in a MWBC in metallic conduit with 4 wires (3 phases A,B,C and a neutral) considered a CCC????

That depends if the majority of the load is non-linear or not.

If the majority of the load is non-linear than the NEC requires we treat the neutral as a CCC due to harmonic currents on the neutral.
 