This kind of expands on the sticky thread at the top of this forum,
[h=3]Understanding the Neutral Conductor[/h]
So we're building a machine for a customer. Some of the equipment in the rack requires 208 since it pulls enough current that 120 would be a pain. They wanted to use a 120V UPS to run the computer equipment, and use 208 to run the large power supplies.
We normally don't do that, since modern computers all have universal supplies in them and it's much easier to wire with 208 in the entire rack and just use a 208V supply. We told them as much. They're probably going that way. But it got me thinking, can you run a 120V load on one leg of a double pole breaker, and still retain wire protection for the neutral lead using a double pole breaker?
With a split phase (residential) system where L1 and L2 are 180 degrees out of phase, the answer is obviously "yes" since the loads on each leg cancel eachother out:
But what about 208 where the phases are 120 degrees out? Can the current on the neutral leg exceed the breaker rating? The answer is no, it cannot. Here is the worse case scenario, where each leg has a full 20A load on it. The neutral return has the sum of both currents on it, and does not exceed the max of each leg (I'll be honest, I had to graph this before I got my head around it):
So that answers the question, no you cannot overload the neutral conductor by using each leg of the double pole breaker using max load to a single neutral conductor.
That said, I'm curious if anything in the NEC covers this? Can you install a 120V outlet on a double pole breaker?
[h=3]Understanding the Neutral Conductor[/h]
So we're building a machine for a customer. Some of the equipment in the rack requires 208 since it pulls enough current that 120 would be a pain. They wanted to use a 120V UPS to run the computer equipment, and use 208 to run the large power supplies.
We normally don't do that, since modern computers all have universal supplies in them and it's much easier to wire with 208 in the entire rack and just use a 208V supply. We told them as much. They're probably going that way. But it got me thinking, can you run a 120V load on one leg of a double pole breaker, and still retain wire protection for the neutral lead using a double pole breaker?
With a split phase (residential) system where L1 and L2 are 180 degrees out of phase, the answer is obviously "yes" since the loads on each leg cancel eachother out:
But what about 208 where the phases are 120 degrees out? Can the current on the neutral leg exceed the breaker rating? The answer is no, it cannot. Here is the worse case scenario, where each leg has a full 20A load on it. The neutral return has the sum of both currents on it, and does not exceed the max of each leg (I'll be honest, I had to graph this before I got my head around it):
So that answers the question, no you cannot overload the neutral conductor by using each leg of the double pole breaker using max load to a single neutral conductor.
That said, I'm curious if anything in the NEC covers this? Can you install a 120V outlet on a double pole breaker?