kosullivan
Member
- Location
- Alpharetta, GA
We are considering pulling a new set of three individual 4KV - 750 MCM cables (1 per phase + a #2 ground wire) (1000+ feet) through a 30 year old spare conduit that passes through five existing buried 6 ft x 6 ft. pull boxes that have existing energized 4KV cables in several conduits running through them. We blew out the conduits with air and pull a 4" rat through all the conduits.
One member of the design team is saying that it is okay to pull through the pull boxes as long as we install insulated blankets around the energized conductors. Another member is saying that we need to fully de-energize / ground out all the existing energized conductors before entering the pull boxes. I am reading over NFPA 70E 130.xxx and 20 CFR 1910.333 trying to determine which method is OSHA appropriate.
I downloaded a "Pulling Calculator" from www.southwire.com and watched the www.Polywater.com pulling videos on You Tube (GREAT Info) but will pose the "pulling questions" in another question.
Any comments or suggestions would be appreciate.
Thank you for your time.
Kevin O.
One member of the design team is saying that it is okay to pull through the pull boxes as long as we install insulated blankets around the energized conductors. Another member is saying that we need to fully de-energize / ground out all the existing energized conductors before entering the pull boxes. I am reading over NFPA 70E 130.xxx and 20 CFR 1910.333 trying to determine which method is OSHA appropriate.
I downloaded a "Pulling Calculator" from www.southwire.com and watched the www.Polywater.com pulling videos on You Tube (GREAT Info) but will pose the "pulling questions" in another question.
Any comments or suggestions would be appreciate.
Thank you for your time.
Kevin O.