I gotta run the combined AC output of 3 inverters up and over a roof 50' and at least 4 @ 90 degree bends to the ACD.
Would you, instead, run the individual INV output circuits (6 @ #3 THWN-2 CU hots plus neutral plus EGC) then combine at end of above run next to ACD ?
or...........
combine inverter outputs at inverters then run the mongo 4/0 (250A circuit, so maybe 250 kcmil) to ACD?
Spaghetti = 1-1/2" EMT min.
Beefy wires = 2" EMT min.