Pulling tension - 12kV primary 1/0 Al

Status
Not open for further replies.

GISdude

Member
Location
Sacramento, CA
Hi all,
I'm trying to figure out the pulling tension for a 381' run. When starting at a XFRM and and pulling to a 90deg elbow, is it acceptable to say that the initial tension at the XFRM is zero? Or should I put a small tension(say25lbs) at that point? This is going to be a 3phase run that will terminate at a primary pull box - all the elbows added together is over 270deg. Yes, the crew will hate me, but it's got to be done.

I've already used an online calculator (thanks SOUTHWIRE) and did a manual calc and they are reasonable close.

Thanks,
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The crew should be pushing the conductors into the raceway at the feed end, but that does not always happen, so I would use some tension at the feed end.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
If the cable drum at the entrance is about 2 m away from the first duct, the weight of one meter of cable will be Tin-I think.
 