Pulling Through Equipment

Status
Not open for further replies.

Atomant

Member
Can service conductors be pulled from the load side of a utility meter, through a nipple to a disconnect and continue on through a second nipple to a manual transfer switch? The load side of the MTS conductors would then leave the MTS and re-enter the disconnect where they would enter the building (the panel is back-to-back). The service is a 200A 208/120V 3 Phase System and all conduits and nipples are sized properly.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Does this answer your question ?

230.7 Other Conductors in Raceway or Cable.
Conductors other than service conductors shall not be installed in the same service raceway or service cable.
 