Pulling wire through strip lighting

Status
Not open for further replies.

wiley_5150

New member
I am installing strip lighting which are connected end to end. I am pulling the wire through the fixtures from one end to the other. Someone on the job site told me you can not do this anymore. Is this trued?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You can run from one end to the other if the circuit is feeding the strip lights. There are some additional permissions granted in 410.65.

Welcome to the forum.
 

480sparky

Senior Member
Location
Iowegia
410.64 says it's permitted only if the luminaire is listed for such use.

And welcome to the fourm!
emoticons_spot_party.gif
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I agree with Rob,

Provided that the circuit is supplying the luminaires, the luminaire need not be listed as a raceway in accordance with 410.65.

410.64 would apply if you are running multiple circuits through the luminaires or a single circuit that does not supply the luminaire.

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
That only addresses specific luminaires ('designed for end-to-end connection.....'). 410.64 is more broad in it's coverage.

I would agree with you if 410.65 only contained the first sentence up to the word "or". "Luminaires connected together by recognized wiring methods" would cover the fixtures mentioned in the OP.
 